Yaskawa VS-606V7 - Alarm przeciążenia po 2-3 minutach pracy

Guna 15 Cze 2017 02:48 1188 1
  • #1 16530646
    Guna
    Poziom 6  
    My inverter yaskawa vs-606v7 showing over load alarm.when i start run its okey but after 2-3 minutes its show that alarm.
  • Pomocny post
    #2 16530841
    premiks
    Poziom 15  
    Hello.
    Inverter displays >oL1 or oL2?
    OL1 (Motor overload)
    Motor overload
    protection operates by
    built-in electronic thermal
    overload relay.
    • Check the load size or
    V/f pattern setting
    (constants n011 to n017)
    • Set the motor rated
    current shown on the
    nameplate by constant
    n036.
    OL2 (Inverter overload)
    Inverter overload
    protection operates by
    built-in electronic thermal
    overload relay.
    • Check the load size or
    V/f pattern setting
    (constants n011 to n017)
    • Check the inverter
    capacity.